Post by SDL on Nov 13, 2018 14:05:13 GMT -8
Hi Buckwester,
I'd especially like to see SunControl in the same situation. That would help me understand what is going on.
Looks like your battery is pretty well charged up. Nothing coming from solar of course. Note: You are drawing current through the Load and it is only slightly charging the battery. SunAIrPlus and SunControl have different controller chips so they will behave differently. I would *guess* this has something to do with your power supply and SunAIrPlus is prioritizing supporting the load rather than charging. What happens when you disconnect the load?
BP
|
|
|
Post by buckwestern on Nov 14, 2018 10:03:43 GMT -8
SunAirPlus board
Prior to AC disconnect:
SunAirPlus Currents / Voltage ----------------- LIPO_Battery Bus Voltage: 4.10 V LIPO_Battery Shunt Voltage: 0.04 mV LIPO_Battery Load Voltage: 4.10 V LIPO_Battery Current 1: 0.40 mA Battery Power 1: 0.00 W
Solar Cell Bus Voltage 2: 0.76 V Solar Cell Shunt Voltage 2: 0.00 mV Solar Cell Load Voltage 2: 0.76 V Solar Cell Current 2: -0.00 mA Solar Cell Power 2: -0.00 W
Output Bus Voltage 3: 4.96 V Output Shunt Voltage 3: 29.60 mV Output Load Voltage 3: 4.96 V Output Current 3: 296.00 mA Output Power 3: 1.47 W
After AC disconnect:
SunAirPlus Currents / Voltage ----------------- LIPO_Battery Bus Voltage: 0.00 V LIPO_Battery Shunt Voltage: 41.32 mV LIPO_Battery Load Voltage: 0.04 V LIPO_Battery Current 1: 413.20 mA Battery Power 1: 0.02 W
Solar Cell Bus Voltage 2: 0.05 V Solar Cell Shunt Voltage 2: 0.00 mV Solar Cell Load Voltage 2: 0.05 V Solar Cell Current 2: -0.00 mA Solar Cell Power 2: -0.00 W
Output Bus Voltage 3: 4.96 V Output Shunt Voltage 3: 29.56 mV Output Load Voltage 3: 4.96 V Output Current 3: 295.60 mA Output Power 3: 1.47 W
|
|
|
Post by buckwestern on Nov 14, 2018 10:12:36 GMT -8
SunControl board:
Prior to AC disconnect:
SunAirPlus Currents / Voltage ----------------- LIPO_Battery Bus Voltage: 4.10 V LIPO_Battery Shunt Voltage: 9.36 mV LIPO_Battery Load Voltage: 4.11 V LIPO_Battery Current 1: 93.60 mA Battery Power 1: 0.38 W
Solar Cell Bus Voltage 2: 0.58 V Solar Cell Shunt Voltage 2: 0.00 mV Solar Cell Load Voltage 2: 0.58 V Solar Cell Current 2: -0.00 mA Solar Cell Power 2: -0.00 W
Output Bus Voltage 3: 5.11 V Output Shunt Voltage 3: 27.80 mV Output Load Voltage 3: 5.11 V Output Current 3: 278.00 mA Output Power 3: 1.42 W
After AC disconnect:
SunAirPlus Currents / Voltage ----------------- LIPO_Battery Bus Voltage: 0.00 V LIPO_Battery Shunt Voltage: 36.96 mV LIPO_Battery Load Voltage: 0.04 V LIPO_Battery Current 1: 369.60 mA Battery Power 1: 0.01 W
Solar Cell Bus Voltage 2: 0.04 V Solar Cell Shunt Voltage 2: 0.00 mV Solar Cell Load Voltage 2: 0.04 V Solar Cell Current 2: -0.00 mA Solar Cell Power 2: -0.00 W
Output Bus Voltage 3: 5.11 V Output Shunt Voltage 3: 27.80 mV Output Load Voltage 3: 5.11 V Output Current 3: 278.00 mA Output Power 3: 1.42 W
|
|
|
Post by SDL on Nov 14, 2018 10:20:42 GMT -8
Looks right on both counts.
SunAirPlus is not charging the battery at 4.11 V, but they are two different solar controller chips.
Take SunAirPlus and disconnect the load and show that. That will help me figure what is going on.
BP
|
|
|
Post by buckwestern on Nov 14, 2018 10:31:24 GMT -8
Looks right on both counts. SunAirPlus is not charging the battery at 4.11 V, but they are two different solar controller chips. Take SunAirPlus and disconnect the load and show that. That will help me figure what is going on. BP I did...it is the post right above the SunControl board.
|
|
|
Post by SDL on Nov 14, 2018 11:57:53 GMT -8
The Output Load is still connected on both of those postings.
BP
|
|
|
Post by buckwestern on Nov 14, 2018 18:43:14 GMT -8
it is? I pulled the AC and then copied the output
|
|
|
Post by buckwestern on Nov 14, 2018 18:48:24 GMT -8
you can see the battery bus voltage goes to 0
|
|
|
Post by buckwestern on Nov 15, 2018 8:46:37 GMT -8
shut it down and rebooted with just the battery:
SunControl board:
SunAirPlus Currents / Voltage ----------------- LIPO_Battery Bus Voltage: 4.10 V LIPO_Battery Shunt Voltage: 35.72 mV LIPO_Battery Load Voltage: 4.13 V LIPO_Battery Current 1: 357.20 mA Battery Power 1: 1.48 W
Solar Cell Bus Voltage 2: 0.00 V Solar Cell Shunt Voltage 2: 0.00 mV Solar Cell Load Voltage 2: 0.00 V Solar Cell Current 2: -0.00 mA Solar Cell Power 2: -0.00 W
Output Bus Voltage 3: 5.11 V Output Shunt Voltage 3: 27.68 mV Output Load Voltage 3: 5.11 V Output Current 3: 276.80 mA Output Power 3: 1.42 W
|
|
|
Post by buckwestern on Nov 15, 2018 8:54:57 GMT -8
I shut it down again, replaced the SunControl board with the SunAirPlus board and rebooted with just the battery:
SunAirPlus board:
SunAirPlus Currents / Voltage ----------------- LIPO_Battery Bus Voltage: 0.00 V LIPO_Battery Shunt Voltage: 40.52 mV LIPO_Battery Load Voltage: 0.04 V LIPO_Battery Current 1: 405.20 mA Battery Power 1: 0.02 W
Solar Cell Bus Voltage 2: 0.00 V Solar Cell Shunt Voltage 2: 0.00 mV Solar Cell Load Voltage 2: 0.00 V Solar Cell Current 2: -0.00 mA Solar Cell Power 2: -0.00 W
Output Bus Voltage 3: 4.96 V Output Shunt Voltage 3: 29.40 mV Output Load Voltage 3: 4.96 V Output Current 3: 294.00 mA Output Power 3: 1.46 W
|
|
|
Post by SDL on Nov 15, 2018 18:09:33 GMT -8
It "looks" like it is working well.
What I need you to do is remove the Output Load (The Raspberry Pi), plug in the Raspberry Pi to a different power source and then re-run the tests with the usb power in plugged in and not plugged in.
Then I can see if there is a problem with the USB power in. I think that the controllers are just behaving differently, but this will show me what is going on.
BP
|
|
|
Post by buckwestern on Nov 15, 2018 18:39:53 GMT -8
OK, I am not sure what you want me to do, but let me take a shot at it:
1. plug SunAirPlus and SunControl into AC power 2. leave connections from Sun* board to GroverI2C 3. plug Pi into separate AC power
correct?
|
|
|
Post by buckwestern on Nov 16, 2018 11:11:59 GMT -8
with SunAirPlus configured as above:
SunAirPlus Currents / Voltage ----------------- LIPO_Battery Bus Voltage: 4.10 V LIPO_Battery Shunt Voltage: 0.00 mV LIPO_Battery Load Voltage: 4.10 V LIPO_Battery Current 1: 0.00 mA Battery Power 1: 0.00 W
Solar Cell Bus Voltage 2: 0.38 V Solar Cell Shunt Voltage 2: 0.00 mV Solar Cell Load Voltage 2: 0.38 V Solar Cell Current 2: -0.00 mA Solar Cell Power 2: -0.00 W
Output Bus Voltage 3: 2.17 V Output Shunt Voltage 3: 0.00 mV Output Load Voltage 3: 2.17 V Output Current 3: 0.00 mA Output Power 3: 0.00 W
|
|
|
Post by SDL on Nov 17, 2018 12:29:12 GMT -8
Buckwestern,
Perfect. Now repeat the same with SunControl. It looks like your SunAirPlus shuts down charging at 4.10V.
BP
|
|
|
Post by buckwestern on Nov 19, 2018 6:52:32 GMT -8
Repeated with SunControl as requested. Interesting that the same battery was used for this test and it appears to be charging. Was the SunAirPlus not charging it completely?
SunAirPlus Currents / Voltage ----------------- LIPO_Battery Bus Voltage: 4.10 V LIPO_Battery Shunt Voltage: -5.92 mV LIPO_Battery Load Voltage: 4.09 V LIPO_Battery Current 1: -59.20 mA Battery Power 1: -0.24 W
Solar Cell Bus Voltage 2: 0.42 V Solar Cell Shunt Voltage 2: 0.00 mV Solar Cell Load Voltage 2: 0.42 V Solar Cell Current 2: -0.00 mA Solar Cell Power 2: -0.00 W
Output Bus Voltage 3: 5.11 V Output Shunt Voltage 3: 0.44 mV Output Load Voltage 3: 5.11 V Output Current 3: 4.40 mA Output Power 3: 0.02 W
|
|